7 , . . , , .
, , ( ) . . .
: 2 (~160)
:
:
:
: /
, , . . .
- , . . added value .
, , , forum .
, ( , , ) , (/), . , .
: . , , .
: , , ( ) . / , .
(, , ) , , . .
Hint: . , :
1. --
2.
3. fine tunning .
, , SUV.
1. 24 .
2. ,
3.
1 & 2 . , . start/stop on/off PID .
3, , 26-27 20-21 , 8 19 , . , , . , . .
-
.
:
, . .
: . , , . .
: , ().
;
() .
: .
1: 3
K2: 3,8
3: 3,4
4: 3,5
5: 4,5
6: 0 ( ;))
38 33 = 5 .
:
= (1+2+3+4+5) = (3+3,8+3,4+3,5+4,5) = 18,2 ltr/min
18,2 * 60 = 1092 ltr/h
1092 / 1000 = 1,092 m3/h
= * = 1092 * 5 = 5460 cal
5460 * 1,163 = 6349 Watt 6,3 kW
50, : 6349 / 50 = 127 Watt/ m2
. , .
Hint: . IR , . +/- 0,5 , ( ) ( ) .
: 1000
, . ON/OFF PID , . , . , ( ). .
Last edited by aNodyNos; 09-12-2013 at 17:14:46.
-
: () . . 3D Google Sketchup free ware. (Edit: 9Mb zipped ).
, /. / . ( ) . T . .
. setup . , , . setup . display .
: / , . . , /.
, ; .
: 35 2 m3/h /. ( 1 m3/h ), 1 2 35 /. 1 2 ( full ) /.
( /) " 30 " " 1 1 m3/h 1. , 1 m3/h 35 2 . / , , . , / . 100% ( On/Off ) /, / , . (100% ) (100% ) ( (/x) + (/y)). , , , >= .
, , , , . .
( /) < (1 + 2) , ( 2), 35 . . ܔ / inverter / start/stop .
/ min max / . min - max . min 1,1 m3/h max 3,6 m3/h / 2,1 m3/h.
Auto Manual 100%, / / . fine tunning . / 1 2 . .
; / , (buffer) . :)
. / / .
Last edited by aNodyNos; 09-12-2013 at 17:52:00.
-
: ( ) ( ) . .
setup ( /), 1 = 80 2 = 60 80 , 1 2 60 . .
: . , ( ). On/Off PID , . Watt . full, / . , ;0)
: . . , / , ( ) SCOP (Seasonal Coefficient of Performance) /.
. , kWh.
Hint_1: / / .
Hint_2: , ( ).
(/): . / (/). , .
/ /; / minimum . / / start/stop. / / minimum . , /, COP . / ( 100 - 150 ) .
Hint_1: / , , /, / , /.
Hint_2: A / , , / " / / . .
: .
Last edited by aNodyNos; 09-12-2013 at 20:36:37.
-
: if/then ( if/then PLC ( ). . minimum , .
40 0 10 10 31 .
open loop setup marmao. closed loop, . . . .
Hint: , . , . . vs . 24/7 , , 1 0 ( on off).
Inverter: , , full . . soft start .
Hint: inverter / kWatt minimum maximum . minimum inverter inverter , start/stop . inverter Hitachi .
( ) /. , / forum - :) -
setup , SCOP / > 3,5.
.
1. / start/stop inverter
2. / ( SCOP)
3.
1 / ( ) / , 2.
full ( on full open) / . 5 .
/ 3.
, . ( ).
. ( )
. 1 2
.
( /) /. 100% .
2-3 . fine tunning self learning 12 , .
/ 1 . / / SCOP .
( ) . start/stop .
. kWh SCOP / 3,5.
90 , , , 130 , 23 22 3,5 , .
/ .
:0)